A shunt is often listed as an optional extra when you buy your solar regulator. Plasmatronics sell theirs in two parts – the shunt and something called the shunt adapter. In my experience very few people understand the function of this device and more importantly why it is an important part of your motorhome or caravan solar setup.
From this photo of a shunt you can see that it is a fairly simple device, no moving parts and no electronics. How can this lump of brass actually perform any useful function?
Simply put, a shunt translates “current flowing” into a voltage signal. The voltage produced by a shunt is exactly proportional to the amount of current flowing through it. For example if 10amps is flowing from your solar panels to the battery (through your shunt) – this will produce a voltage of 1 millivolt at the small terminals of the shunt.. The same shunt will produce 2 millivolts when 20 amps is flowing through the shunt. This same setup will produce
negative 3 millivolts when the batteries are discharging (at night for example). This is a really useful thing when it comes to reporting what is going on with your solar power and battery system.
We could of course measure the current directly (with a ammeter)– but to do this we would need to use heavy cables (capable of carrying the load and charge current) all the way to and from the measurement device. It is far easier to run tiny wires to carry a voltage signal that is proportional to the current; then just measure this voltage.
When is a shunt required?
If you want to accurately track the state of your batteries (how charged they are), the best way to do this is to count all the energy that is removed from the battery and count all the energy that is added (by the solar panels). This involves measuring the current flowing in the wire going to the battery. Remember – a shunt cannot report energy that it does not see. This is one of the most common mistakes I see in motorhome and caravan wiring. If your system has a shunt, one side must be connected DIRECTLY to the battery terminal and there must be NO other cables attached to that battery terminal. To attach cables to the battery terminal that the shunt is connected to is to by-pass the shunt.
The PL40 solar controller can measure and track a small load directly (without a shunt) when it is attached to the load terminal. This terminal is only rated at 5 amps (20 amps on the PL20). Thus, if you need to measure the current being used by larger loads (inverters etc) you need to fit a shunt.
The state of charge (SOC) display on the PL series of regulators is meaningless unless a shunt is correctly fitted.
Shunts are rated with two sets of figures written as “200A = 200mV”. The first number is the maximum current that the shunt can handle – this is typically 100 or 200 amps. The second figure tells us how much voltage will be produced when the shunt is carrying this maximum current. So a shunt marked 200A = 200mV will carry a maximum of 200 amps and when it is doing so, it will produce 200milli-volts across the measurement terminals.
It is important to make sure that the regulator is expecting to see and understands how to read the voltage that your particular shunt produces. The shunt adapter supplied as an optional extra for the PL series of regulators has three settings that allow it to work with most common shunts.
Some tips in installing your shunt.
- Make sure you are using the correct shunt for your setup. See the information that came with the regulator.
- Make sure you do not exceed the rating of the shunt – it will get very hot very quickly.
- Be absolutely sure that ALL the current (both from charge sources AND discharge sources) passes through the shunt. It cannot measure what it can not see.
- Some regulators require the shunt to be installed in the negative battery cable while other regulators require the shunt to be installed in the positive side of the battery. The Plasmatronics PL series do not have any preference. Consult you manual – getting it wrong can damage the regulator.